Installation Specifications

Table: Installation Specifications shows the installation specifications of the ETERNUS DX, and Table: Efficiency and Power Factor of the Power Supply Unit (ETERNUS DX600 S6) and Table: Efficiency and Power Factor of the Power Supply Unit (ETERNUS DX900 S6) show the efficiency and the power factor of the power supply unit.

Table: Installation Specifications

Item

ETERNUS DX600 S6

ETERNUS DX900 S6

ETERNUS DX8900 S6

Dimensions

(W × D × H)

Frontend enclosure

482 × 805 × 217 mm (5U)

Controller enclosure

482 × 785 × 132 mm (3U)

Drive enclosure

2.5" NVMe type

481 × 546 × 88 mm (2U)

2.5" SAS type

482 × 540 × 88 mm (2U)

3.5" SAS type

482 × 560 × 88 mm (2U)

Power distribution unit

1U

482 × 111 × 44 mm

2U (*1)

(485 × 123 × 44 mm) × 2 (2U)

Maximum weight

Frontend enclosure (*2)

58kg

Controller enclosure (*2)

55kg

Drive enclosure (*2)

2.5" NVMe type

33kg

2.5" SAS type

35kg

3.5" SAS type

35kg

Power distribution unit

1U

2.5kg

2U (*1)

(3.0kg) × 2

Power

Voltage

AC 200 – 240V

Phase

Single

Frequency

50Hz/60Hz

Maximum power consumption

AC 200 – 240V

Frontend enclosure (*3)

580W (610VA)

630W (680VA)

Controller enclosure (*3)

1,503W (1,505VA)

1,761W (1,763VA)

Drive enclosure (*3)

2.5" NVMe type

570W (580VA)

2.5" SAS type

430W (440VA)

3.5" SAS type

340W (350VA)

Maximum heat generation

AC 200 – 240V

Frontend enclosure (*3)

2,090kJ/h

2,270kJ/h

Controller enclosure (*3)

5,420kJ/h

6,340kJ/h

Drive enclosure (*3)

2.5" NVMe type

2,060kJ/h

2.5" SAS type

1,600kJ/h

3.5" SAS type

1,300kJ/h

Maximum amount of exhaust air

Frontend enclosure

7.0m3/min

Controller enclosure

5.3m3/min

Drive enclosure (*4)

2.5" NVMe type

3.9m3/min

2.5" SAS type

4.0m3/min

3.5" SAS type

4.0m3/min

Environmental conditions

Temperature

Operating

10 – 40°C

10 – 35°C

Not operating

0 – 50°C

During shipment

-25 – 60°C

Temperature gradient

15°C/Hr or less

Humidity

Operating

20 – 80%RH

Not operating

8 – 80%RH

During shipment

8 – 90%RH

Humidity gradient

30%/day or less

Maximum wet bulb temperature

29°C

Altitude above sea level

0 – 3,000m

Airborne dust

0.15mg/m3 or less

Gas concentration tolerance level

Cl2: 6.8ppb or less, H2S: 7.1ppb or less,

SO2: 37.5ppb or less, NH3: 423.5ppb or less,

NO2: 52.3ppb or less, O3: 5ppb or less,

HCl: 6.6ppb or less, HF: 3.6ppb or less

Oil vapor

0.2mg/m3 or less

Seawater (salt corrosion)

If the ETERNUS DX is installed on the ocean or premises within 0.5km from the coast, necessary measures must be taken to prevent salt corrosion.

Vibration limit

Operating

400gal

Not operating

1,000gal

Noise emission

Sound power level

7.9B (*5)

8.1B (*6)

*1

A 2U power distribution unit is composed of two 1U power distribution units.

*2

Maximum weight of an enclosure where all installable options are installed.

*3

The power consumed and heat generated under maximum load when all installable options are installed in the enclosure.

*4

This value is for each drive enclosure when the following are installed.

  • For 2.5" NVMe type drive enclosures, 24 drives

  • For 2.5" SAS type drive enclosures, 24 drives

  • For 3.5" SAS type drive enclosures, 12 drives

*5

This value is measured when a single controller enclosure and three 2.5" NVMe type drive enclosures are configured in an environment in which the temperature is 23 ± 2°C at 0 meters above sea level.

*6

This value is measured when a single frontend enclosure, two controller enclosures and two 2.5" NVMe type drive enclosures are configured in an environment in which the temperature is 23 ± 2°C at 0 meters above sea level.

Table: Efficiency and Power Factor of the Power Supply Unit (ETERNUS DX600 S6)

Component name

80PLUS®

Efficiency

Power factor

Output

20% (*1)

50% (*1)

100% (*1)

50% (*1)

Controller enclosure

TITANIUM (*2)

94.9%

96.1%

94.9%

0.995

Single output

Drive enclosure

2.5" NVMe type

PLATINUM (*2)

91.1%

94.3%

93.2%

0.990

Multiple output

2.5" SAS type

91.7%

94.4%

93.7%

0.974

3.5" SAS type

*1

Indicates the load factor against the rated output of the PSU.

*2

The component uses power supply units equivalent to those that are certified as 80PLUS® PLATINUM or higher for the power saving program for electrical equipment promoted by the 80PLUS® program.

Table: Efficiency and Power Factor of the Power Supply Unit (ETERNUS DX900 S6)

Component name

80PLUS®

Efficiency

Power factor

Output

20% (*1)

50% (*1)

100% (*1)

50% (*1)

Frontend enclosure

TITANIUM (*2)

94.9%

96.1%

94.9%

0.995

Single output

Controller enclosure

94.9%

96.1%

94.9%

0.995

Drive enclosure

2.5" NVMe type

PLATINUM (*2)

91.1%

94.3%

93.2%

0.990

Multiple output

2.5" SAS type

91.7%

94.4%

93.7%

0.974

3.5" SAS type

*1

Indicates the load factor against the rated output of the PSU.

*2