Installation Specifications
Table: Installation Specifications shows the installation specifications of the ETERNUS DX, and Table: Efficiency and Power Factor of the Power Supply Unit (ETERNUS DX600 S6) and Table: Efficiency and Power Factor of the Power Supply Unit (ETERNUS DX900 S6) show the efficiency and the power factor of the power supply unit.
Item |
ETERNUS DX600 S6 |
ETERNUS DX900 S6 |
ETERNUS DX8900 S6 |
|||
---|---|---|---|---|---|---|
Dimensions (W × D × H) |
Frontend enclosure |
— |
482 × 805 × 217 mm (5U) |
|||
Controller enclosure |
482 × 785 × 132 mm (3U) |
|||||
Drive enclosure |
2.5" NVMe type |
481 × 546 × 88 mm (2U) |
||||
2.5" SAS type |
482 × 540 × 88 mm (2U) |
|||||
3.5" SAS type |
482 × 560 × 88 mm (2U) |
|||||
Power distribution unit |
1U |
482 × 111 × 44 mm |
— |
|||
2U (*1) |
(485 × 123 × 44 mm) × 2 (2U) |
|||||
Maximum weight |
Frontend enclosure (*2) |
— |
58kg |
|||
Controller enclosure (*2) |
55kg |
|||||
Drive enclosure (*2) |
2.5" NVMe type |
33kg |
||||
2.5" SAS type |
35kg |
|||||
3.5" SAS type |
35kg |
|||||
Power distribution unit |
1U |
2.5kg |
— |
|||
2U (*1) |
(3.0kg) × 2 |
|||||
Power |
Voltage |
AC 200 – 240V |
||||
Phase |
Single |
|||||
Frequency |
50Hz/60Hz |
|||||
Maximum power consumption |
AC 200 – 240V |
Frontend enclosure (*3) |
— |
580W (610VA) |
630W (680VA) |
|
Controller enclosure (*3) |
1,503W (1,505VA) |
1,761W (1,763VA) |
||||
Drive enclosure (*3) |
2.5" NVMe type |
570W (580VA) |
||||
2.5" SAS type |
430W (440VA) |
|||||
3.5" SAS type |
340W (350VA) |
|||||
Maximum heat generation |
AC 200 – 240V |
Frontend enclosure (*3) |
— |
2,090kJ/h |
2,270kJ/h |
|
Controller enclosure (*3) |
5,420kJ/h |
6,340kJ/h |
||||
Drive enclosure (*3) |
2.5" NVMe type |
2,060kJ/h |
||||
2.5" SAS type |
1,600kJ/h |
|||||
3.5" SAS type |
1,300kJ/h |
|||||
Maximum amount of exhaust air |
Frontend enclosure |
— |
7.0m3/min |
|||
Controller enclosure |
5.3m3/min |
|||||
Drive enclosure (*4) |
2.5" NVMe type |
3.9m3/min |
||||
2.5" SAS type |
4.0m3/min |
|||||
3.5" SAS type |
4.0m3/min |
|||||
Environmental conditions |
Temperature |
Operating |
10 – 40°C |
10 – 35°C |
||
Not operating |
0 – 50°C |
|||||
During shipment |
-25 – 60°C |
|||||
Temperature gradient |
15°C/Hr or less |
|||||
Humidity |
Operating |
20 – 80%RH |
||||
Not operating |
8 – 80%RH |
|||||
During shipment |
8 – 90%RH |
|||||
Humidity gradient |
30%/day or less |
|||||
Maximum wet bulb temperature |
29°C |
|||||
Altitude above sea level |
0 – 3,000m |
|||||
Airborne dust |
0.15mg/m3 or less |
|||||
Gas concentration tolerance level |
Cl2: 6.8ppb or less, H2S: 7.1ppb or less, SO2: 37.5ppb or less, NH3: 423.5ppb or less, NO2: 52.3ppb or less, O3: 5ppb or less, HCl: 6.6ppb or less, HF: 3.6ppb or less |
|||||
Oil vapor |
0.2mg/m3 or less |
|||||
Seawater (salt corrosion) |
If the ETERNUS DX is installed on the ocean or premises within 0.5km from the coast, necessary measures must be taken to prevent salt corrosion. |
|||||
Vibration limit |
Operating |
400gal |
||||
Not operating |
1,000gal |
|||||
Noise emission |
Sound power level |
7.9B (*5) |
8.1B (*6) |
*1 | : | A 2U power distribution unit is composed of two 1U power distribution units. |
*2 | : | Maximum weight of an enclosure where all installable options are installed. |
*3 | : | The power consumed and heat generated under maximum load when all installable options are installed in the enclosure. |
*4 | : | This value is for each drive enclosure when the following are installed.
|
*5 | : | This value is measured when a single controller enclosure and three 2.5" NVMe type drive enclosures are configured in an environment in which the temperature is 23 ± 2°C at 0 meters above sea level. |
*6 | : | This value is measured when a single frontend enclosure, two controller enclosures and two 2.5" NVMe type drive enclosures are configured in an environment in which the temperature is 23 ± 2°C at 0 meters above sea level. |
Component name |
80PLUS® |
Efficiency |
Power factor |
Output |
|||
---|---|---|---|---|---|---|---|
20% (*1) |
50% (*1) |
100% (*1) |
50% (*1) |
||||
Controller enclosure |
TITANIUM (*2) |
94.9% |
96.1% |
94.9% |
0.995 |
Single output |
|
Drive enclosure |
2.5" NVMe type |
PLATINUM (*2) |
91.1% |
94.3% |
93.2% |
0.990 |
Multiple output |
2.5" SAS type |
91.7% |
94.4% |
93.7% |
0.974 |
|||
3.5" SAS type |
*1 | : | Indicates the load factor against the rated output of the PSU. |
*2 | : | The component uses power supply units equivalent to those that are certified as 80PLUS® PLATINUM or higher for the power saving program for electrical equipment promoted by the 80PLUS® program. |
Component name |
80PLUS® |
Efficiency |
Power factor |
Output |
|||
---|---|---|---|---|---|---|---|
20% (*1) |
50% (*1) |
100% (*1) |
50% (*1) |
||||
Frontend enclosure |
TITANIUM (*2) |
94.9% |
96.1% |
94.9% |
0.995 |
Single output |
|
Controller enclosure |
94.9% |
96.1% |
94.9% |
0.995 |
|||
Drive enclosure |
2.5" NVMe type |
PLATINUM (*2) |
91.1% |
94.3% |
93.2% |
0.990 |
Multiple output |
2.5" SAS type |
91.7% |
94.4% |
93.7% |
0.974 |
|||
3.5" SAS type |
*1 | : | Indicates the load factor against the rated output of the PSU. |